1. Welcome to Hvacproforums, an interactive community exclusively for HVAC professionals. The collective years of HVAC experience and the knowledge our forum members share make this an invaluable resource for those in the HVAC industry. We have a lot of fun, but make no mistake, we are pros. Hvacproforums is self supporting ...there are NO advertisers here. Do-it-yourselfers and Homeowners are encouraged to seek information elsewhere. Those involved in the HVAC industry are urged to register. its 100% free and easy, Once registered you will have access to the technical forums, Be sure to click over to the new members forum and introduce yourself after registering!

Intellipak compressor trip

Discussion in 'Commercial' started by iceout70, May 17, 2017.

  1. iceout70

    iceout70 New Member

    Messages:
    11
    Customer reset unit twice and it was running when I got there all looks good. The manual does not say much any ideas?

    Sent from my XT1254 using Tapatalk
     
  2. pecmsg

    pecmsg Junior my ASS

    Messages:
    19,382
    Location:
    Eastern LI
    Keep resetting until something blows up
     
    Bustawrench likes this.
  3. iceout70

    iceout70 New Member

    Messages:
    11
    I can't it runs fine

    Sent from my XT1254 using Tapatalk
     
  4. jays 65

    jays 65 New Member

    Messages:
    280
    had a account those intellipacks about drove me crazy every week would randomly trip on something
     
  5. Seacurrent

    Seacurrent New Member

    Messages:
    10
    Look in the history and see what caused the last 2 trips.

    Sent from my SM-G920V using Tapatalk
     
    Bustawrench likes this.
  6. iceout70

    iceout70 New Member

    Messages:
    11
    All it says is compressor trip and the previous one was a bas trip

    Sent from my XT1254 using Tapatalk
     
  7. NZ All Blacks Fan

    NZ All Blacks Fan Just Another swinging Dick

    Messages:
    9,241
    Location:
    West Coast - Canada
    check power supply - look for low/high voltages check connection slook for burnt/overheating connections

    575/600v units are notorious for crankcase heater issues
     
  8. iceout70

    iceout70 New Member

    Messages:
    11
    I will check it out thanks

    Sent from my XT1254 using Tapatalk
     
  9. Seacurrent

    Seacurrent New Member

    Messages:
    10
    There's usually 3 things that give that trip if I remember correctly. The wiring diagram should show you high pressure, over current and, compressor temp sensor. My experience has been that it is usually a faulty overload or bad temp sensor. When it is only an occasional nuisance trip I put "tattletale" type fuses across the safeties to determine where the trip is coming from.

    Sent from my SM-G920V using Tapatalk
     
  10. iceout70

    iceout70 New Member

    Messages:
    11
    I will check each one thanks

    Sent from my XT1254 using Tapatalk
     
  11. Tap

    Tap i hate it when a velociraptor throws poop at me

    Messages:
    10,218
    Location:
    Lost
    Pull the terminal cover on the compressors after you kill power to the unit you most likely will see a small round peckerhead with two terminals just below the main peckerhead, make sure those connections are tight if there is any play or corrosion clean em up/ put new terminals on the wires. Also check the aux's on the contactors if it calls for a compressor and the aux doesn't send a closure to the controls it will alarm i just cant remember what alarm it is. There's also some contacts behind the factory breakers on some of those units that also will send an alarm and lock out that circuit if it doesn't see closure as it thinks the breaker is tripped.


    Good Luck and god speed :mrbill:
     
    Jim54, Seacurrent and frozensolid like this.
  12. frozensolid

    frozensolid Psychologist's Dream

    Messages:
    11,833
    Location:
    Earth
    Tighten the Compressor and Contactor terminals. Also ohm out contactor coil(s)
     
    Tap and Jim54 like this.
  13. Jim54

    Jim54 New Member

    Messages:
    236
    Location:
    Addison, Tx.
    Compressor trip? Which compressor? Put it in test mode and run eveything. Try to get something to fail in front of you. Are all of your condenser fan motors running? (High head trip) Any burnback on the compressor wiring both in the terminal box or contactors
    ( High amp draw/winding sensor trip)? Contactors ok? Connections good on safeties (high ohms trip)? Compressor circuit breakers ok on must hold/must trip? Sometimes it can take a bit to pin it down.
     
  14. pintofstout

    pintofstout New Member

    Messages:
    1,462
    Location:
    Olean, NY
    This trip is very vague. It consists of the safety chain (as noted in the manual) which goes to the scroll board, the scroll board itself, and one more thing they don't mention anywhere.... The aux relays on the contactors.

    Really annoying that a tripped breaker takes out the entire circuit of cooling btw....