1. Welcome to Hvacproforums, an interactive community exclusively for HVAC professionals. The collective years of HVAC experience and the knowledge our forum members share make this an invaluable resource for those in the HVAC industry. We have a lot of fun, but make no mistake, we are pros. Hvacproforums is self supporting ...there are NO advertisers here. Do-it-yourselfers and Homeowners are encouraged to seek information elsewhere. Those involved in the HVAC industry are urged to register. its 100% free and easy, Once registered you will have access to the technical forums, Be sure to click over to the new members forum and introduce yourself after registering!

Low discharge super heat yciv177

Discussion in 'Commercial' started by cookr68, May 15, 2017.

  1. cookr68

    cookr68 New Member

    Messages:
    15
    Can anyone tell me the cause of low doscharge superheay on yciv 177

    Sent from my SM-N920V using Tapatalk
     
  2. heavyevans

    heavyevans FNG

    Messages:
    1,162
    Location:
    Indy
    Typically low suction superheat lowers discharge superheat. Check evaporator approach and verify all temperature sensors are reading correctly. On the one I remember, It was the suction line sensor reading about 20° too high. York makes some pretty chitty sensors.
     
    cookr68, jamesyarbrough and Zman like this.
  3. 22blood

    22blood red wire nuts only

    Messages:
    1,586
    Look at the evap coil before pressures

    If high suction low head pressure its your compressor
     
    cookr68 likes this.
  4. Tap

    Tap i hate it when a velociraptor throws poop at me

    Messages:
    10,218
    Location:
    Lost
    Verify sensors as heavyevans said, definitely check evap approach/ water flow, discharge sh oil temp etc log the entire chiller, it may have a stuck open txv, starting flooded, slide valve could be getting stuck and not unloading. Read the IOM spend some time with her youll figure it out.
     
    somedude likes this.
  5. Zman

    Zman Hanging by a Thread

    Messages:
    276
    Location:
    The "I know a Guy" State
    The Problem is that model is made only for the Dominican Republic Region and some South American Countries.This is why Doscharge and Superheay do not compute on your Standard OssWipe Mannyfold Gaugis!
     
    somedude likes this.
  6. 22blood

    22blood red wire nuts only

    Messages:
    1,586
    Say that again pardner
     
  7. cookr68

    cookr68 New Member

    Messages:
    15
    Zman actually took the time to type that lol, sorry i was driving when i typed that. I am actually from houston i normally say thats "brt" (beeg round thang) aint workin.

    Sent from my SM-N920V using Tapatalk
     
  8. Zman

    Zman Hanging by a Thread

    Messages:
    276
    Location:
    The "I know a Guy" State
    I was just messing around at the end of long day.Didnt think your Post was serious with that spelling.Hope you get it figured out...oh,and Don't text and Drive,thats How Bad Text Happen!:D
     
    somedude likes this.
  9. cookr68

    cookr68 New Member

    Messages:
    15
    Thanks zman great advice !

    Sent from my SM-N920V using Tapatalk
     
  10. 22blood

    22blood red wire nuts only

    Messages:
    1,586
    Bant camp
     
  11. cookr68

    cookr68 New Member

    Messages:
    15
    Heavyevans , thank you very much, i will check it out.

    Sent from my SM-N920V using Tapatalk
     
  12. pintofstout

    pintofstout New Member

    Messages:
    1,462
    Location:
    Olean, NY
    Either low suction superheat or low overall compression will cause that, as well as head pressure or discharge temperature sensor calibrations..... But i think an underperforming compressor will also generate something similar to a low lift alarm.


    Sent from my iPhone using Tapatalk
     
    cookr68 likes this.
  13. cookr68

    cookr68 New Member

    Messages:
    15
    Hey all, we found a bad suction line temp sensor.

    Sent from my SM-N920V using Tapatalk
     
    somedude likes this.
  14. somedude

    somedude Senior Stalker & PITA, aka zachhvac

    Messages:
    3,327
    Location:
    Los Alamos California
    Problem is its a york